Hi, i would like to know how to scal analogic inputs in a DL-205, which directions i have to use??? Thanks


  • adccommunitymod (AutomationDirect)

    Created Date: May 12,2005

    Created by: carane

    Hi, i would like to know how to scal analogic inputs in a DL-205, which directions i have to use???

    Thanks

  • adccommunitymod (AutomationDirect)

    Created Date: May 12,2005

    Created by: rex2802

    H-L

    Units = A -------

    4095

    H = High limit of the engineering unit range

    L = Low limit of the engineering unit range

    A = Analog value (0-4095)

  • adccommunitymod (AutomationDirect)

    Created Date: May 12,2005

    Created by: rex2802

    Sorry it didn't post the way I typed it.

    H-L/4095*A

  • adccommunitymod (AutomationDirect)

    Created Date: May 13,2005

    Created by: Tom Jenkins

    For any unit conversion on any PLC you can use four function math with the following,which asumes integer math:

    DataOffset = Data in input register at 4 mA or zero analog signal of whatever range - for example 0 VDC on a 0-10 VDC transmitter)

    DataSPan = Data at 20 mA - Data @ 4 mA

    FACTOR = arbitrary factor (multiple of 10)needed to get proper resolution and accuracy

    EU = Engineering Units x FACTOR

    EUOffset = Engineering Units @ 4 mA x FACTOR

    EUSpan = (Engineering Units @ 20 mA -Engineering Units @ 4 mA) x FACTOR

    DATA = Actual data reading in input register

    EU = ((EUSpan x (DATA - DataOffset))/DataSpan) + EUOffset

    ProcessValue = EU / FACTOR

    For Example, 0-60 psig from 4-20 mA with resolution of 0.1 psig:

    FACTOR = 10

    Data @ 4 mA = 6240

    Data @ 20 mA = 31208

    DataOffset = 6240

    DataSpan = 31208 - 6240 = 24968

    EUOffset = 0 x 10 = 0

    EUSpan = (60 - 0) x 10 = 600

    DATA = 18975

    EU = ((600 x (18975 - 6240)) / 24968) + 0 = 306

    Process Value = 306 / 10 = 30.6 psig

    You would use the normal math functions to accomplish this. Just make sure you do your diovides AFTER the multiplies.