adccommunitymod (AutomationDirect) asked a question.

CPU in endless Loop

Created Date: February 22,2005

Created By: polybus

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I wrote an endless loop in error on a DL06 . It faulted in the run mode and would not communicate. After powering down for 20 minute the fault condition was still there. Moving the Mode switch to stop did not work ether. I had to un-soder the battery /Super-Cap to clear the fault. Is there an easier way. Thanks Steve


  • adccommunitymod (AutomationDirect)

    Created Date: February 22,2005

    Created by: polybus

    I wrote an endless loop in error on a DL06 . It faulted in the run mode and would not communicate. After powering down for 20 minute the fault condition was still there.

    Moving the Mode switch to stop did not work ether.

    I had to un-soder the battery /Super-Cap to clear the fault. Is there an easier way.

    Thanks

    Steve

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 22,2005

    Created by: franji1

    Did you move the switch to TERM (middle) or to STOP? It needs to be in STOP, then try powering down, then turning it back on with switch in STOP position. Is this what you did?