putting 2 or more D2-250 port 2 on network & PC

Created Date: December 16,2002

Created By: polarbearcp

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am looking into putting several D2-250s on a network and looking at being able to program monitor with a PC. What is the best route? And can I share data over the same communication network?


  • adccommunitymod (AutomationDirect)

    Created Date: December 17,2002

    Created by: RHanrahan

    Probably the easiest thing to do would be to put ECOM Modules in each rack and connect them all using a hub. Give each ECOM MOdule its own IP address and away you go. I use DSData to communicate with the various PLCs. You can also communicate directly using DirectSoft.

  • adccommunitymod (AutomationDirect)

    Created Date: December 17,2002

    Created by: franji1

    ECOMs allow peer-to-peer communication (anyone can talk to anyone) which is good if you want a PC to communicate with the PLCs AND have the PLCs share data.

    Serial ports must be configured as master only or slave only, so it's a little difficult to configure a peer network using serial ports. It's doable, but more of a hassle.

  • adccommunitymod (AutomationDirect)

    Created Date: December 16,2002

    Created by: polarbearcp

    I am looking into putting several D2-250s on a network and looking at being able to program monitor with a PC. What is the best route? And can I share data over the same communication network?