Can I change Drive Parameter P 3.00 from the PLC? I want the PLC to tell the drive whether to accept instructions from itself or the manual devices wired to its inputs. If I set P3.00 to 01 or 02, can the PLC communicate and change it to 03 or 04 and back?
Created Date: November 14,2002
Created by: tdahlstrom
Can I change Drive Parameter P 3.00 from the PLC? I want the PLC to tell the drive whether to accept instructions from itself or the manual devices wired to its inputs. If I set P3.00 to 01 or 02, can the PLC communicate and change it to 03 or 04 and back?
Created Date: November 18,2002
Created by: Carl@ADCsupport
You can write to parameter 3.00 via modbus rtu. It is 0300H (40769).
There are no restrictions that I'm aware of.
Carl
Created Date: November 18,2002
Created by: tdahlstrom
Thanks for the response. I am having trouble with RS232 Communications. I set up counters according to the manual to detect communications errors and it is indicating constant errors even though the drive does accept commands. Also the drive flashes ce03. I have double checked the values I am trying to send and everything seems is order. Any ideas?