I am using a dl05 with analog input to read current through a 4-20ma 0-50 amp curren transformer. The problem is when a scale the value at a specific amperage, when I adjust the amperage the read value doesn't coincide any more. The further I move the further it goes away from the real value. I am measuring a split-wave current, and the device is reading in RMS. I am scaling using the formula (v2000 * 500 / 4095)+8(to a line with house standard) Ron


  • adccommunitymod (AutomationDirect)

    Created Date: November 07,2000

    Created by: schneire

    I am using a dl05 with analog input to read current through a 4-20ma 0-50 amp curren transformer.

    The problem is when a scale the value at a specific amperage, when I adjust the amperage the read value doesn't coincide any more. The further I move the further it goes away from the real value.

    I am measuring a split-wave current, and the device is reading in RMS.

    I am scaling using the formula

    (v2000 * 500 / 4095)+8(to a line with house standard)

    Ron

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: November 07,2000

    Created by: Tom Jenkins

    Skip the +8. V2000 will = 0 at 4 mA and 4095 at 20 mA. Assuming your transmitter and C/T are accurate the formula is:

    Amps = V2000 x 500 / 4095 This will give results with an implied one decimal place (amps + tenths). Make sure you do the multiply before the divide to maintain accuracy.

    You may have a problem with the C/T. Sometimes on low ratio C/Ts (like a 50:5 C/T) the allowable burden is very low, and even a few dozen feet of #14 AWG wire can be more resistance at high amperge than the C/T can handle. Check the total loop resistance at the C/T, including the transmitter burden. Check your PLC readings against the mA signal and use a clamp on ammeter to check your C/T output.