Does anyone have a good document or diagram to connect multiple devices to an RS485 drop? I am using a BRX PLC, and for the first time, attempting a multi-drop on the BRX's 485 terminals. Even though its only two devices, I don't want to cheap out and just buy the 2nd RS485 port for the plug-able BRX port.


  • adccommunitymod (AutomationDirect)

    Created Date: February 10,2018

    Created by: dslusser

    Does anyone have a good document or diagram to connect multiple devices to an RS485 drop?

    I am using a BRX PLC, and for the first time, attempting a multi-drop on the BRX's 485 terminals. Even though its only two devices, I don't want to cheap out and just buy the 2nd RS485 port for the plug-able BRX port.

  • adccommunitymod (AutomationDirect)

    Created Date: February 11,2018

    Created by: pbw

    You can enable 120 ohm termination on the PLC in the configuration menu.

    You will have to set a unique device ID for each slave.

    Hope this helps.

  • adccommunitymod (AutomationDirect)

    Created Date: February 12,2018

    Created by: dslusser

    So just parallel the 3 wires, and enable the terminator?

    Sounds good to me.

  • adccommunitymod (AutomationDirect)

    Created Date: February 12,2018

    Created by: bcarlton

    Be sure to use RS485 rated cable. If you are sure you have everything hooked up correctly and parameters set correctly and still don't have communication swap 'A ' and 'B ' connections at one end. Verify with a master and one slave at first for multiple slave connections.