adccommunitymod (AutomationDirect) asked a question.

Modbus/RTU and TCP/IP

Created Date: September 17,2012

Created By: Richardv

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a system with 4 DL260's communicating via a Modbus/RTU network all connected to Port 2 on the processors. Is it possible to add an ECOM100 to the Master PLC and have it connect to a 5th device via Modbus TCP/IP while the PLC is still acting as the Master on the RTU network This 5th device wants to be a master when connected to a Modbus/RTU but I don't really want to rewrite the software for the system.


  • adccommunitymod (AutomationDirect)

    Created Date: September 17,2012

    Created by: Do-more PE

    Sure. That should not be a problem.

  • adccommunitymod (AutomationDirect)

    Created Date: September 17,2012

    Created by: Richardv

    I have a system with 4 DL260's communicating via a Modbus/RTU network all connected to Port 2 on the processors.

    Is it possible to add an ECOM100 to the Master PLC and have it connect to a 5th device via Modbus TCP/IP while the PLC is still acting as the Master on the RTU network

    This 5th device wants to be a master when connected to a Modbus/RTU but I don't really want to rewrite the software for the system.

    Expand Post