adccommunitymod (AutomationDirect) asked a question.

Little Problem

Created Date: March 29,2008

Created By: amos

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a dl06 master talking to a dl06 slave using Ibox ecomm100wx.In the to slave destination I enter VC20 at the remote address. When using ecomm protocol in netedit it works just fine. I change the protocol to modbus tcp it times out. I changed vc20 to c20 then it works just fine using both protocols. I was just wondering if this is normal? It was confusing because I couldn't figure why it didn't work using modbus. Entering v40620 in the field also defaults the vc20. Amos


  • adccommunitymod (AutomationDirect)

    Created Date: March 31,2008

    Created by: GKiser

    This doesn't make sense. It should work regardless of whether you use ECOM protocol or Modbus TCP protocol. However, perhaps you are looking in the wrong place, because:

    V40620 = VC400 (not VC20)

    V40601 = VC20

    When using ECOM protocol, WX-ing to VC20 actually means write to VC20 in the slave, because the slave is always another ECOM.

    However, when using Modbus TCP protocol it is a bit different, but the result should be the same. In Modbus TCP, the ECOM100 translates VC20 into a WX to V40601, but because you have a Peer-to-peer configuration in the ECOM100 for Modbus TCP, it translates this write into Modbus parameters.

    40601 (octal) --> 16769 (decimal)

    Thus this WX VC20 means a Modbus FC16 (Preset Multiple Registers) to Holding Register 56770 (40001 + 16769).

    However, since the slave is also an ECOM100 it translates this FC16 to Holding Register 56770 as a write to VC20.

    Thus it should work both ways. Mine does when I experiment with it here.

    Greg Kiser

    Host Engineering, Inc.

    support@hosteng.com

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 01,2008

    Created by: amos

    Thank You Greg for your reply.

    I saw my error after I posted but that that wasn't the problem. The real situation was when communicating using Ecomm protocol I was talking to a ECOMM not ECOMM100. When talking modbus Tcp I was talking to a Lantronix UDS10 IAP I just changed the IP Address. Using your example what would the difference be if you would have used c20 instead of vc20?

    Thank You, Amos

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 01,2008

    Created by: GKiser

    If you had used a WX C20, then this would get converted to an FC15 (Force Multiple Coils) at Modbus Coil Address of 3089. This is because mapping is listed as:

    For WX:

    GY0-GY3777 (FC15: Coils 1-2048)

    Y0-Y1777 (FC15: Coils 2049-3072)

    C0-C3777 (FC15: Coils 3073-5120)

    S0-S1777 (FC15: Coils 5121-6144)

    T0-T377 (FC15: Coils 6145-6400)

    CT0-CT377 (FC15: Coils 6401-6656)

    Thus, C20 = FC15: Coil 3089.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 01,2008

    Created by: amos

    Thanks Greg

    I think I can see what the problem was. The address must have been too large for the lantronix to use.

    Thanks for the help

  • adccommunitymod (AutomationDirect)

    Created Date: March 29,2008

    Created by: amos

    I have a dl06 master talking to a dl06 slave using Ibox ecomm100wx.In the to slave destination I enter VC20 at the remote address. When using ecomm protocol in netedit it works just fine. I change the protocol to modbus tcp it times out. I changed vc20 to c20 then it works just fine using both protocols. I was just wondering if this is normal? It was confusing because I couldn't figure why it didn't work using modbus. Entering v40620 in the field also defaults the vc20.

    Amos