Can a Slave PLC Sense a Comm Failure?

Created Date: January 17,2007

Created By: dc

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

If you have a Master DL-06 simply READING values from a Slave DL-06 through Port 2, is there any way the slave PLC can determine a communication failure. In other words, is there a special bit for Port 2 that I can monitor for a period of time and if the bit does not become true, then the slave PLC can assume there has been a Communication Failure. If there are any suggestions, please pass them my way.


  • adccommunitymod (AutomationDirect)

    Created Date: January 17,2007

    Created by: Andy

    There is no special bit in the slave mode but you can build your own watchdog timer. Just have the master set a bit in the slave. Then once the slave acknowledges it have the slave reset it. If the master does not set it within a certain time frame then the slave can consider it a comm failure.

    Hope this helps

  • adccommunitymod (AutomationDirect)

    Created Date: January 17,2007

    Created by: dc

    If you have a Master DL-06 simply READING values from a Slave DL-06 through Port 2, is there any way the slave PLC can determine a communication failure.

    In other words, is there a special bit for Port 2 that I can monitor for a period of time and if the bit does not become true, then the slave PLC can assume there has been a Communication Failure.

    If there are any suggestions, please pass them my way.