adccommunitymod (AutomationDirect) asked a question.

DO-DCM

Created Date: October 13,2006

Created By: Pero

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Can I use AIN block to read port 2 form additional DO-DCM communication port on DL06 PLC? I programmed communication parameter in lader logic but I can not set the port number in AIN. Only port 2 form integrated communication port is allowed in AIN blok.


  • adccommunitymod (AutomationDirect)

    Created Date: October 13,2006

    Created by: Tech Guy

    This feature is not currently available. A future release of DirectSoft will enable this support.

  • adccommunitymod (AutomationDirect)

    Created Date: October 13,2006

    Created by: Pero

    How then can I receive ASCII data from DO-DCM on DL-06 PLS? I need to communicate with weather station and the integrated port is already occupied.

  • adccommunitymod (AutomationDirect)

    Created Date: October 13,2006

    Created by: FACTSTech

    The F0-CP128 BASIC CoProcessor could be programmed to interface to your ASCII device. Note that the function of the F0-CP128 is dictated entirely by the BASIC program that you write and load into the module. This is not a plug and play module.

  • adccommunitymod (AutomationDirect)

    Created Date: October 13,2006

    Created by: Pero

    Can I use AIN block to read port 2 form additional DO-DCM communication port on DL06 PLC? I programmed communication parameter in lader logic but I can not set the port number in AIN. Only port 2 form integrated communication port is allowed in AIN blok.