COM PORT HELP!!

Created Date: March 14,2006

Created By: squills

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

hello, iam new to these PLCS, My question was is there anyway to sent the port 2 back to the default.. my problem is at first i could connect with no problems, i went to plc mode and changed acouple things. trying to make the plc work for modbus. well for some reason i changed the address to 5 i belive but not sure. now i get the can not connect to plc. I have tried a lot the connection says disabled in yellow.. anyone help??? its a DL06


  • adccommunitymod (AutomationDirect)

    Created Date: March 14,2006

    Created by: Tech Guy

    The easy way would be to get a communication cable for port 1. This port is always fixed at 9600 baud and odd parity.

  • adccommunitymod (AutomationDirect)

    Created Date: March 15,2006

    Created by: squills

    ok i tryed to connect to com port 1 with the phone line. i connected one side to my laptop and the other to port 1 when i connect it dials my number. should it be dialing a different number. i still can not connect with the erreor trying to connect to unlocked device.also if by chance i did change the address which i dont think i did. Woudl i still be able to connect to comport 1 with address 1?

    thanks for help..

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 15,2006

    Created by: jackson

    Port 1 of the PLC is NOT for a modem connection. It is a serial port. Connecting this port to your modem will not work. You need to purchase the D2-DSCBL cable from Automationdirect to connect from the 9 pin serial port of your laptop to the RJ12 port of the PLC.

    It is possible that you have damaged the port of the PLC with this connection.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: March 15,2006

    Created by: marksji

    Or make your own cable by following the wiring diagram in the manual.

  • adccommunitymod (AutomationDirect)

    Created Date: May 03,2006

    Created by: ThermoT

    Are you using Directsoft?

  • adccommunitymod (AutomationDirect)

    Created Date: March 14,2006

    Created by: squills

    hello, iam new to these PLCS, My question was is there anyway to sent the port 2 back to the default.. my problem is at first i could connect with no problems, i went to plc mode and changed acouple things. trying to make the plc work for modbus. well for some reason i changed the address to 5 i belive but not sure. now i get the can not connect to plc. I have tried a lot the connection says disabled in yellow.. anyone help???

    its a DL06

    Expand Post