adccommunitymod (AutomationDirect) asked a question.

com issues

Created Date: February 20,2006

Created By: ewomack

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am new to using automation. I am using a dl205 with a 260cpu with an erm modual and a ecom 100 to connect to 4 e-drv cards and 4 gs2 drives. I cannot get Directsoft to recognize the cpu or to get communications established. Netedit does see all of the components.


  • adccommunitymod (AutomationDirect)

    Created Date: February 20,2006

    Created by: GKiser

    I assume you are trying to use DirectSOFT and make a link to the H2-ECOM100 module. (It can't connect to the H2-ERM, nor the EDRV). So, when you attempt to make a link, exactly what error message are you getting? Also, if you can see the H2-ECOM100 in NetEdit, you can right-click on it and select "CPU Test " from the menu. What result do you get there?

    Greg Kiser

    Host Engineering, Inc.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 20,2006

    Created by: ewomack

    I am new to using automation. I am using a dl205 with a 260cpu with an erm modual and a ecom 100 to connect to 4 e-drv cards and 4 gs2 drives. I cannot get Directsoft to recognize the cpu or to get communications established.

    Netedit does see all of the components.