
adccommunitymod (AutomationDirect) asked a question.
Created Date: October 03,2003
Created By: eagleelectric
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
Just a note to give some insite on how we got the DL450 to talk with a remote DL06 via MDS1710 Radios. The cables are straight through....TX-TX RX-RX CTS-CTS RTS-RTS GRND-GRND. Set the CTS Delay in the PLCS to 5ms Set the Slave Radios to 50ms Delay and the master to the max delay 255ms. We are polling 6 RTUs (DL06) on a simplex (same TX RX Freq.) system. Works fine. It took 2 days and a lot of tech support from both manufacturers but in the end it was a joint effort from a lot of minds. Hope this helps someone.
Created Date: October 03,2003
Created by: eagleelectric
Just a note to give some insite on how we got the DL450 to talk with a remote DL06 via MDS1710 Radios. The cables are straight through....TX-TX RX-RX CTS-CTS RTS-RTS GRND-GRND. Set the CTS Delay in the PLCS to 5ms Set the Slave Radios to 50ms Delay and the master to the max delay 255ms. We are polling 6 RTUs (DL06) on a simplex (same TX RX Freq.) system. Works fine. It took 2 days and a lot of tech support from both manufacturers but in the end it was a joint effort from a lot of minds. Hope this helps someone.