RS485 Modbus Slave with 250 CPU

Created Date: October 19,2001

Created By: DJE Design

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

It seems to me that the bottom port of the 250 CPU could be used on a 3 wire Modbus system without utilizing an RS232 to RS485 converter (or 422 to 485). You would, as in remote I/O, wire TXD+ to RXD+ and TXD- to RXD-. If the 250 were a Modbus slave, the transmitter would necessarily have to Tri-State (high-impedence) except when responding. Has anyone tried this?


  • adccommunitymod (AutomationDirect)

    Created Date: October 24,2001

    Created by: Mike McClanahan

    The port is Modbus Protocol. Modbus is not a hardware standard but is a communications protocol specification. The port on the 250 is still following the RS-232 standard which is +/- 15V for on and off, not high impedance. Besides why risk damaging the communications port and having to replace the CPU because of a ground loop current problem from a power hit when an inexpensive RS-485 converter solves the problem and can provide some protection at the same time.

    Mike

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 19,2001

    Created by: DJE Design

    It seems to me that the bottom port of the 250 CPU could be used on a 3 wire Modbus system without utilizing an RS232 to RS485 converter (or 422 to 485).

    You would, as in remote I/O, wire TXD+ to RXD+ and TXD- to RXD-. If the 250 were a Modbus slave, the transmitter would necessarily have to Tri-State (high-impedence) except when responding.

    Has anyone tried this?

    Expand Post