adccommunitymod (AutomationDirect) asked a question.
Created Date: January 25,2016
Created By: DetroitSound
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I have built an exhaust fan system using GS2-41P0 drives. I have one issue. I want to set it up in such a way that the drive limits itself to the motor current I have it programmed with, regardless of the speed settings. The way it is now it will go to maximum then it kicks out into overload because it is drawing too much current, making the entire system unreliable. I want the drive to refuse to give the motors too much power so they will continue running, at the maximum performance the drive and motor are capable of. I would much rather have it running too slow and limiting itself than to have it try to run full speed and trip out on overload. Is there a programming parameter for this?
Created Date: January 25,2016
Created by: mwdkmpr
I have never done this but I think you should be able to use the analog output terminals (P4.11) to give feedback to the drives analog input. Look at example 5 on page 4-39 to see how to setup a drive for reduced output with an increased analog input.
Created Date: January 25,2016
Created by: Cow
I looked through the manual, and didn't see a setting. As a workaround, if you set 3.11 or 3.12 to 08, you will get an output you can monitor from the drive that your motor is over it's current setpoint, 3.17.
Is your motor and fan setup sized properly? It sounds like too much fan or not enough motor HP?
Created Date: January 26,2016
Created by: DetroitSound
Set P6.10 and P6.11 to (Motor nameplate current / Drive current rating) * 100%. The default is 150% drive rated current which could lead to tripping on sustained overload.
E.g. if your motor nameplate is 2.4A and the 41P0 is rated 3.0 amps then
2.4/3 *100 = 0.8 * 100 = 80 for P6.10 and P6.11
Thank you. I would have gone with a 2HP motor and drive, as I recall one or the other was not available at the time, but I'm with 1 hp, like it or not...
I'll make those changes today...
Created Date: April 19,2016
Created by: cheme
I have a similar application to this running at work. What I did was setup a PID instruction using the desired motor amps as the set point and the drive frequency as the output. It has been working very well. It is setup on a blower application that has a varying amount of vapor load that often times requires more horsepower than is available so when that occurs, the speed is reduced to keep the motor at is FLA.
Created Date: August 18,2016
Created by: DetroitSound
First of all, the P6.10 and P6.11 resolved that problem. Now I have a problem that seems to occur - not every time, but most of the time. It happens too often, this system has to be reliably operable by "mechanically declined " people.
During shutdown, it trips with an OV (Over Voltage) fault, which locks the drives out until it is reset. Quick rehash of my equipment - each fan has a MTR-001-3BD18 Iron Horse motor; wiring is approximately 50 feet, 3 #12 THHN wires in 1/2 " EMT, then at the drive end they connect to LR-41P0 Line Reactors, then the line reactors are connected to the GS2-41P0 drives. The system operates at 480 volts 3 phase. It looks real pretty!
I have tried the following:
P1.00 Ramp to stop and coast to stop. It faults either way.
P1.02 Deceleration Time: I 've tried 30 to 360 seconds
P1.04 Decel S-Curve: I 've tried 0 (linear) and 1-7. 0 seems to be the worst and 7 seems to be the best, but it still trips out even on 7.
P6.04 (AVR) - I have tried all four choices
P6.05 (over voltage stall prevention) I have tried it enabled and disabled.
P6.06 (Auto Adjustable accel / decel) I have tried all four choices.
P6.07 (Over Torque detection mode) I have tried 00 and 01
P6.31 to P6.36 (fault record) all show 02 (over voltage).
Might anyone have suggestions? I programmed the Click PLC for future addition of a C More Micro Touch through a RS-485 link, then you could select speeds with that. Since I already have the output module wired to the GS2 and all I would have to do is change the programming in the Click, I am considering slowing it down by steps, give it time to stabilize at each step, take it down another notch, then shut it off after the 10% (6hz) step.
Created Date: August 18,2016
Created by: scott.lawrence
If the line reactor is on the line side of the drive, it's possible that the OV is caused by regen from the fan.
From the manual, pg 6-3...
3. Bus over-voltage may also be caused by motor
regeneration. Either increase the decel time or add an
optional braking resistor.
Created Date: August 18,2016
Created by: Mike Nash
Coast to stop should not in any way be allowing an OV trip. Are you sure the fan has come to a stop before the drive is told to start again? I would think with coast to stop (which turns off the output transistors) the only was to see an OV is if the AC line increased (unlikely) or if you were getting a run input again before the motor stopped. If that is the problem, you could prove it by disconnecting the start signal until the motor is stopped. Without DC Injection at start or speed search, starting into a moving fan is difficult at best.
Created Date: August 19,2016
Created by: DetroitSound
Coast to stop should not in any way be allowing an OV trip. Are you sure the fan has come to a stop before the drive is told to start again? I would think with coast to stop (which turns off the output transistors) the only was to see an OV is if the AC line increased (unlikely) or if you were getting a run input again before the motor stopped. If that is the problem, you could prove it by disconnecting the start signal until the motor is stopped. Without DC Injection at start or speed search, starting into a moving fan is difficult at best.
I would think so too, but this has proven not to be the case, it trips with an OV trip even if it is set to coast to stop. Once it is told to stop it won't be started again until the next day, if at all (depending on the weather). The line reactor is between the motor and the drive. The reactor does get hot in operation. It is approximately 175 ' from this location to the breaker panel where the 480v circuit originates and between 50-60 feet to the fans.
This is how I have it set up. The top cabinet has the disconnect, line fuses, reactors and control transformer. The lower cabinet has the drives, drive input fuses, the Click and its power supply, and of course, the switches and indicators. Actually, both cabinets get pretty warm in operation and I want to add cooling fans.
The fans are started early in the day and they remain on until near the end of the work day, or until the outside conditions are unfavorable to where we need to run the air conditioning or heat, so they are normally turned on and off only once during the day. Other than the trip at shutdown it works perfectly.
Running them at "coast to stop " brings them from full speed to full stop in about 45 seconds. I do not care how long it takes to stop, 10 seconds or 10 minutes, it's all good.
n102419
Created Date: August 19,2016
Created by: Mike Nash
I'm probably in the add-a-db-resistor camp also at this point. You could have something wonky with line voltage happening. I have seen issues with power factor correction capacitors installed elsewhere in a plant causing issues. I 've also seen transformers saturating causing high peaks - seen with an oscilloscope, but meters didn't show it.
Created Date: August 21,2016
Created by: andremholmes
Have you tried using dampers to reduce to air flow? the motor could be working too hard.