adccommunitymod (AutomationDirect) asked a question.
GS-2 JOG
Created Date: January 28,2008
Created By: twbrock
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I have set Parameter 3.03 to 09 5.00 to 6.0 I have run contacts to DCM and DI1 to run FWD I have jog contacts to DCM and DI3 to JOG Are these correct. The manual is clear as mud. Thanks TWBrock
Created Date: January 29,2008
Created by: milldrone
twbrock,
From the manual page 4-25
Note: The Jog Command cannot be used when the motor is running. The motor must be
stopped to initiate this command.
Also you use only the programmed input (DI3 in your case) do not use the DI1 input also at the same time.
Vaughn
Created Date: January 29,2008
Created by: twbrock
Thanks for the reply
I thought thats what the manual said but its not real clear
Thanks again
Tommy