adccommunitymod (AutomationDirect) asked a question.

Drive analog out to PLC

Created Date: May 20,2003

Created By: John K Neiswanger

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Looking for input on the simplest/cleanest way to take the analog output from a SJ100 drive to a DL205 system. Looks like either analog in with the PWM output from the drive or counter in from the pulse output from the drive. Any pros/cons either way?


  • adccommunitymod (AutomationDirect)

    Created Date: June 16,2003

    Created by: Carl@ADCsupport

    You would need to use the FA-4PWM to get the analog signal to the plc. You could always build a filter circuit. The description is on page 4.29 of the sj100 manual.

    The raw PWM output will not work directly into the plc effectively. My suggestion is to stick with the filtered analog.

    Carl

  • adccommunitymod (AutomationDirect)

    Created Date: May 20,2003

    Created by: John K Neiswanger

    Looking for input on the simplest/cleanest way to take the analog output from a SJ100 drive to a DL205 system. Looks like either analog in with the PWM output from the drive or counter in from the pulse output from the drive. Any pros/cons either way?