
adccommunitymod (AutomationDirect) asked a question.
Created Date: June 27,2012
Created By: Matthew_Luxel
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
Hi all, I currently have an unshielded, normally closed, PNP type capacitive proximity sensor (The sensor is CT1-CP-2A found at the link: http://www.automationdirect.com/static/specs/prox30mmcapct.pdf ) that I want to mount on a parker linear positioner (which is controlled by an MDrive 17 Motor and driver). The range on the capacitive proximity sensor is 20mm. When the motor on the linear stage is powered, however, the capacitive sensor senses the linear stage from about 9cm away. Has anyone else had a similar problem to this? If so are there ways to fix this interference problem? I was thinking of using mu metal ( http://www.mumetal.com/ ) to shield the sensor from the EM field put out from the powered linear stage. Any help would be greatly appreciated. Thank you, Matthew
Created Date: June 27,2012
Created by: Do-more PE
Is the motor ran off of the same 24VDC supply as the Prox?
If not on the same power supply then any chunk of well grounded metal between the motor and prox should provide adequate shielding.
If it is on the same power supply, the the issue may be that the motor is putting too much noise on the power supply and you may need to separate the motor and controls.
Created Date: June 27,2012
Created by: Matthew_Luxel
Hi all,
I currently have an unshielded, normally closed, PNP type capacitive proximity sensor (The sensor is CT1-CP-2A found at the link: http://www.automationdirect.com/static/specs/prox30mmcapct.pdf ) that I want to mount on a parker linear positioner (which is controlled by an MDrive 17 Motor and driver). The range on the capacitive proximity sensor is 20mm. When the motor on the linear stage is powered, however, the capacitive sensor senses the linear stage from about 9cm away. Has anyone else had a similar problem to this? If so are there ways to fix this interference problem? I was thinking of using mu metal ( http://www.mumetal.com/ ) to shield the sensor from the EM field put out from the powered linear stage. Any help would be greatly appreciated.
Thank you,
Matthew
Created Date: June 27,2012
Created by: Matthew_Luxel
Metal shield
Thanks!
The prox and the motor are ran off different power supplies but placing a chunk of metal between the two seemed to work! Thank you for the quick reply!
Best regards,
Matthew Skeels