Hello all, I 've been working with the CLICK PLC for the past couple of months, and I 've been struggling with hooking up an analog IO module. It seems pretty straightforward (just "click " it into place...), but the CLICK software refuses to acknowledge that the module exists. I haven't hot plugged anything, and both the PLC and the module are brand new. I can't imagine what I'm doing wrong. It might seem like a dumb question but... any help? The PLC is C0-11DRE-D and the module is C0-4AD2DA-2. I 've already tried: 1) updating firmware and software 2) ensuring that there's +24V to both the PLC and the IO module Thanks.
Created Date: July 23,2019
Created by: jeb
Hello all,
I 've been working with the CLICK PLC for the past couple of months, and I 've been struggling with hooking up an analog IO module. It seems pretty straightforward (just "click " it into place...), but the CLICK software refuses to acknowledge that the module exists. I haven't hot plugged anything, and both the PLC and the module are brand new. I can't imagine what I'm doing wrong. It might seem like a dumb question but... any help?
The PLC is C0-11DRE-D and the module is C0-4AD2DA-2.
I 've already tried:
1) updating firmware and software
2) ensuring that there's +24V to both the PLC and the IO module
Thanks.
Created Date: July 23,2019
Created by: Garry
https://accautomation.ca/create-an-analog-voltage-input-tester-for-a-plc/
https://www.youtube.com/watch?v=JwSeulaHV6U
Have you looked at the system configuration in the software? Main menu | Setup | System Configuration
You must select the modules that you have connected. This should be selected to match the physical setup and then download into the PLC.
Hope this helps you out.
Regards,
Garry
Created Date: July 23,2019
Created by: jeb
Have you looked at the system configuration in the software? Main menu | Setup | System Configuration
You must select the modules that you have connected. This should be selected to match the physical setup and then download into the PLC.
Thanks for the reply, Garry.
Yes, I 've tried using the system configuration in the software. According to AutomationDirect's tutorial videos, the CLICK should automatically detect the modules that are connected to the PLC and display them in System Config--but mine isn't. Just to be safe, I disconnected from the PLC and selected the analog IO module manually. I reconnected to the PLC, downloaded the project, and got a System Config error when I entered RUN mode. If I try to open the system config when the PLC is connected, the software says there's a discrepancy between the PC and the PLC modules, so I need to pick which one to display. Basically, my problem is that the PLC isn't recognizing that the IO module is attached, so it won't run properly even if the software is configured for an IO module.
Created Date: July 23,2019
Created by: Do-more PE
if the module was plugged in with the PLC powered up, it probably has toasted the backplane chip. Regardless it sounds like the card is dead. It should be seen easily by the software unless the software is ancient.
Created Date: July 23,2019
Created by: jeb
No, I didn't hot plug it. The software is the most recent version, as far as I know. I just downloaded it about a month ago.
The thing that baffles me is that I was having this same problem before, so I finally caved in and contacted the Automation Direct helpdesk directly. They concluded that I had a defective IO module and sent me a new one--but this new one doesn't work, either. I even got a new PLC, thinking that maybe something in my first one was fried, but nope, same deal. I'm really quite perplexed that something that should be so simple is turning out to be so troublesome.
Created Date: July 24,2019
Created by: Do-more PE
What do you have as a power supply? Watts/amps & Volts
Created Date: July 24,2019
Created by: jeb
It's a DC power supply, capable of at least an Amp, maybe more (I'd have to check the specs), and that should be more than enough. I have it set to 24VDC for powering the PLC and the module.
Edit: Just double-checked, the power supply can do 5V at 3A, so it's a 15W supply.
Created Date: July 24,2019
Created by: Do-more PE
5V =/= 24V
Which is it?
Created Date: July 24,2019
Created by: jeb
It's a variable supply, so it can be anything from 0 to about 30VDC. I currently have it set to 24VDC. I know that when it's set to 5V it can deliver up to 3 amps, therefore it's a 15W supply.
Created Date: July 25,2019
Created by: Do-more PE
I would start by trying a different supply, preferably a fixed voltage model. Click really wants good power and that is the only thing you have not changed.