adccommunitymod (AutomationDirect) asked a question.

Multiple supplies for dc inputs?

Created Date: February 07,2017

Created By: pudland

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hi, Looking over the spec sheet for the C0-01DD2-D and it shows 2 separate 24vdc supplies for Y1-Y4 and Y5-Y6. Why can't i use (1) 24v supply for Y1-Y6? I am looking to power 6 small signal reed relays at .012 coil amps per relay? Is it an issue to feed V1 and V2 from the same supply? Thanks, Adam


  • adccommunitymod (AutomationDirect)

    Created Date: February 07,2017

    Created by: pudland

    Hi,

    Looking over the spec sheet for the C0-01DD2-D and it shows 2 separate 24vdc supplies for Y1-Y4 and Y5-Y6. Why can't i use (1) 24v supply for Y1-Y6? I am looking to power 6 small signal reed relays at .012 coil amps per relay? Is it an issue to feed V1 and V2 from the same supply?

    Thanks,

    Adam

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 07,2017

    Created by: Mike Nash

    That's perfectly fine. They are just allowing you flexibility for when you do need to use 2 separate supplies.

  • adccommunitymod (AutomationDirect)

    Created Date: February 07,2017

    Created by: pudland

    Thank you sir!

  • adccommunitymod (AutomationDirect)

    Created Date: February 17,2017

    Created by: pudland

    Can I use a C0-01AC supply both the C0-01DD2-D inputs and outputs? I know i have to watch the current rating of the ps.

    The inputs are contact closures from an external relay.

    The outputs feed 24v small signal relays.

    Thanks,

    Adam

    { "data-align ": "none ", "data-size ": "large ", "data-attachmentid ":104638}

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: February 17,2017

    Created by: kewakl

    Yes, as long as you do as you mention - watch the current ratings.