adccommunitymod (AutomationDirect) asked a question.

Click Ethernet to P2000 using modbus

Created Date: April 04,2017

Created By: highvoltage50

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

i need to sent a 4-40 ma input coming into a click Ethernet to a p2000 using Ethernet and modbus


  • adccommunitymod (AutomationDirect)

    Created Date: April 04,2017

    Created by: highvoltage50

    i need to sent a 4-40 ma input coming into a click Ethernet to a p2000 using Ethernet and modbus

  • adccommunitymod (AutomationDirect)

    Created Date: April 05,2017

    Created by: andremholmes

    Do you mean 4-20mA?

    is the P2K the master?

    The 4-20mA needs to go to click's df location and the P2K grab it from there.

  • adccommunitymod (AutomationDirect)

    Created Date: April 05,2017

    Created by: kewakl

    I don't have experience (or requirement for) of sending/receiving floats between Click and PAC, but bits/words are just fine, and since floats are just an interpretation of a group of bits, it should work.

    Be sure to observe a couple Modbus traps:

    +/- 1 on actual tag address

    word / byte swap

    ---- AND

    If you setup the PAC to READ the value from the CLICK, you would NOT need to assign a Modbus address to the PAC destination tag.

    The Click already has a Modbus address assigned to every location in its address space. Just tell PAC which NODE/address to read from.