adccommunitymod (AutomationDirect) asked a question.

Wiring outputs

Created Date: December 07,2018

Created By: Isakovic

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hello, Just a quick question. I'm using C0-16TD2 modules for outputs (transistor outputs). Should same power supply that is used for powering CPU and inputs be used to power outputs, or I can use other power supply? I know this isn't a problem with inputs because of optical isolation, but I'm not so sure about outputs.


  • adccommunitymod (AutomationDirect)

    Created Date: December 07,2018

    Created by: Isakovic

    Hello,

    Just a quick question. I'm using C0-16TD2 modules for outputs (transistor outputs). Should same power supply that is used for powering CPU and inputs be used to power outputs, or I can use other power supply?

    I know this isn't a problem with inputs because of optical isolation, but I'm not so sure about outputs.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: December 07,2018

    Created by: RogerR

    The same power supply can be used for the CPU, inputs, and outputs.

    There will most likely be more noise on the DC line when this is done, especially if the outputs are inductive loads like relay coils.

    A separate power supply can be used on the outputs when this is a problem.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: December 08,2018

    Created by: Isakovic

    A separate power supply can be used on the outputs when this is a problem.

    That's what I needed. Thanks.