adccommunitymod (AutomationDirect) asked a question.

Click RS-232

Created Date: May 01,2012

Created By: Lonnie

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have managed to get the C-More 3 inch Micro grahics panel working, as well as the SureStep stepper drive system. I have the PC connected to Com1 (developement) but how do I connect HMI and Surestep when I only have 1 spare com2 ( actually 3 using com3 but I want that for a ASCII printout). Is there a solution for this?


  • adccommunitymod (AutomationDirect)

    Created Date: May 01,2012

    Created by: bcarlton

    Yes, cable swapping. Tedious but everything has a limit.

  • adccommunitymod (AutomationDirect)

    Created Date: May 01,2012

    Created by: Lonnie

    Click

    It seem strange to me that the RS232 cannot be daisied chain. I am still in developement designing the system and do want to comunicate with the HMI and the Stepper system while I am monitoring the click responses.

  • adccommunitymod (AutomationDirect)

    Created Date: May 01,2012

    Created by: bcarlton

    With one transmit (which is active all the time) and one receive wire how would you daisy chain it?

    The only method I have seen is a device which receives a message on the receive line. If the message is not meant for its address it replicates the message (with a delay) out the transmit line which may be attached to the receive input of yet another device. If the message is for it then it places its answering message on the transmit line addressed to the requesting unit. It was very slow.

    But this depends on specific units with specifiic protocols (these aren't defined in the RS232 spec)

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: May 01,2012

    Created by: Lonnie

    Click RS232

    In effect I would connect SureStep to port2 and HMI to port1 and have no why of knowing anything about the system since I do not have the laptop to monitor the click.

    I need to adjust the robotic arm while the user UPDATES the HMI to change position on the fly. It would be nice if the SureStep or the HMI had an address that could be dialed in (for each) so that the click could then be monitored while I create safety code

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: May 02,2012

    Created by: Tubecut

    What about RS-485? Is therre someway to use the stepper

    and CLick with HMI?

  • adccommunitymod (AutomationDirect)

    Created Date: May 02,2012

    Created by: bgirouard

    As Tubecut mentioned, how about utilizing the RS-485 port for multiple devices? You would need two things for this: an RS-485 adapter for the Cmore micro EA-MG-SP1 , and a RS-232/RS-485 converter for a Surestep drive. With that, you would be able to apply addressing to both units and still keep two ports open for other communications (PC & ASCII printout).

  • adccommunitymod (AutomationDirect)

    Created Date: May 02,2012

    Created by: Do-more PE

    The Cmore Micro is a mastering device and I am assuming that the PLC would be mastering the SureStep. Only one mastering device is allowed on RS-485 except in very special circumstances.

  • adccommunitymod (AutomationDirect)

    Created Date: May 01,2012

    Created by: Lonnie

    I have managed to get the C-More 3 inch Micro grahics panel working, as well as the SureStep stepper drive system.

    I have the PC connected to Com1 (developement) but how do I connect HMI and Surestep when I only have 1 spare com2 ( actually 3 using com3 but I want that for a ASCII printout).