CLICK Lead Lag Part 2

Created Date: May 14,2013

Created By: rday78

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Ok.. got a good amount of the programming done but running into an issue. I have it so on every call for the pumps to run, it alternates between 2 pumps. However if one of those pumps is not in the auto position, I want it to default to the pump that is in auto everytime not every other cycle. Cant seem to figure it out. Any ideas?

 

**edited by community moderator**

rday78

05-16-2013, 05:33 AM

added file modified e255booster.zip


  • adccommunitymod (AutomationDirect)

    Created Date: May 15,2013

    Created by: milldrone

    if one of those pumps is not in the auto position, I want it to default to the pump that is in auto everytime not every other cycle. Cant seem to figure it out. Any ideas?

    See if this works for you.

  • adccommunitymod (AutomationDirect)

    Created Date: May 16,2013

    Created by: rday78

    Very nice and thank you. By the time I read your post I had worked out a solution. Check it out and see what you think. I like messing with these because there are so many ways to go about solving a problem. Now to work on a flasher circuit for the low suction pressure alarm. Thanks Again!!

  • adccommunitymod (AutomationDirect)

    Created Date: May 16,2013

    Created by: trimixdiver1

    Very nice and thank you. By the time I read your post I had worked out a solution. Check it out and see what you think. I like messing with these because there are so many ways to go about solving a problem. Now to work on a flasher circuit for the low suction pressure alarm. Thanks Again!!

    Dont know about click, but there are special relays SP4, on for 500ms off for 500ms. Throw it in a ladder rung as a contact.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: May 17,2013

    Created by: rday78

    Thanks... I did figure it out tho. Used a self resetting timer for 2 seconds. On equal to 1 it makes output, the other second it stays off. Pretty simple and works great

  • adccommunitymod (AutomationDirect)

    Created Date: May 14,2013

    Created by: rday78

    Ok.. got a good amount of the programming done but running into an issue. I have it so on every call for the pumps to run, it alternates between 2 pumps. However if one of those pumps is not in the auto position, I want it to default to the pump that is in auto everytime not every other cycle. Cant seem to figure it out. Any ideas?