Using data view in edit mode. specified new values for input addresses and selected "write all new values ". Nothing happens after I select Yes to the "Note: ... " Tried this in both Stop and Run Mode. Would like to be able to set these new input values to test program logic and correct output results.


  • adccommunitymod (AutomationDirect)

    Created Date: January 16,2014

    Created by: JLG

    I'm assuming you mean write data (as you 've said), and not write project.

    What data are you specifically trying to write? If there's not much data, you could just set it at first scan.

    Writing data only really makes sense if you have a large data set that the PLC needs to access. You could just create a csv file with the data you need to load and got to PLC> write data into plc.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: January 16,2014

    Created by: Tinker

    Using data view in edit mode. specified new values for input addresses and selected "write all new values ". Nothing happens

    Were these X bits ? usualy the program has precidence over input from the data view, and since the inputs are read every scan the actual phisical state cancels whatever you tried to do with data view. However, there is a way to override that, in the top right of the data view window there is a "View override " check box, if you check that, then a column will be added with "OVR " buttons, if you then click one (or more) of those so it turns yellow you will be able to change the state of a X bit, or other bit that would otherwise be controled by the program.

    Personaly I found the help file rather unhelpful on this point and it took some experimentation before I understood it. Previously, if I was just experimenting with a program I'd repalce X bits with C bits just so I could switch them with data view

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: January 03,2014

    Created by: jnicolosi

    Using data view in edit mode. specified new values for input addresses and selected "write all new values ". Nothing happens after I select Yes to the "Note: ... " Tried this in both Stop and Run Mode.

    Would like to be able to set these new input values to test program logic and correct output results.