Click software (1.10) Timer issues

Created Date: July 16,2011

Created By: Tubecut

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am attaching a PNG file and also the ckp ladder program. A very simple program ( 2 rungs). I have a timer (T1) that the enable rung has two conditions (AND) , C10 and Not T1 (see png file or the ladder program attached). The problem is that enabling the timer by turning ON C10 the timer runs as expected. If I turn OFF C10, the timer continues to increment TD1. I am using only the monitor on line mode and turning ON/OFF C10 using the over write edit mode in the monitor. Question: Is this a bug in the monitor/edit mode or some other bug? Also, in another short test program (file not attached) I had a rung enabled on First Scan to copy a value to DS1. I was unable to edit/change the DS1 value using the monitor edit mode . Thanks in advance for any input. I am thinking that perhaps I am doing something incorrect here but can't 'see ' it :o I am delaying installing the current version (1.31) for the time being. I was hoping to hear some users comments on 1.31 Once again, thanks for any help


  • adccommunitymod (AutomationDirect)

    Created Date: July 16,2011

    Created by: bcarlton

    T1 - you have chosen an OFF DELAY TIMER which times when the input conditions are false.

  • adccommunitymod (AutomationDirect)

    Created Date: July 17,2011

    Created by: Tubecut

    Solved

    Thanks Bernie. I haven't used the off delay timer often.

    The devils in the details :)

  • adccommunitymod (AutomationDirect)

    Created Date: July 16,2011

    Created by: Tubecut

    I am attaching a PNG file and also the ckp ladder program.

    A very simple program ( 2 rungs). I have a timer (T1) that the

    enable rung has two conditions (AND) , C10 and Not T1

    (see png file or the ladder program attached).

    The problem is that enabling the timer by turning ON C10 the

    timer runs as expected. If I turn OFF C10, the timer continues

    to increment TD1.

    I am using only the monitor on line mode and turning ON/OFF

    C10 using the over write edit mode in the monitor.

    Question: Is this a bug in the monitor/edit mode or some other bug?

    Also, in another short test program (file not attached) I had a rung enabled on First Scan to copy a value to DS1.

    I was unable to edit/change the DS1 value using the monitor

    edit mode .

    Thanks in advance for any input. I am thinking that perhaps I am doing something incorrect here but can't 'see ' it :o

    I am delaying installing the current version (1.31) for the time being. I was hoping to hear some users comments on 1.31

    Once again, thanks for any help

    Expand Post