adccommunitymod (AutomationDirect) asked a question.

Click Clock and Calendar

Created Date: December 16,2009

Created By: Dan @ CHP

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Is there a way to adjust the Click PLC clock and calendar from the operating program? I'm installing this PLC as a heating control in a school and would like to give the custodian the ability to reset the clock from the C-more Micro HMI. I also have an automatic Daylight Saving Time routine I'd like to use.


  • adccommunitymod (AutomationDirect)

    Created Date: December 16,2009

    Created by: Tinker

    Well, in the "address picker " all the RTC registers are marked read only. That seems like a flaw to me, no clock in a lowcost PLC is going to be totaly accurate and it is forseeable that it will have to be reset at some time. Maybe they were thinking that since the software is free people will just use the programing software to set the clock, but I'm guessing that your custodian won't be too thrilled with that option. Anyway, since the C-mores are not free, wouln't AD want to give you as many reasons as posible for buying them?

    As far as daylight savings time, you could just add 1 or 0 hour as needed after you read the RTC hour register, without changing the RTC itself.

    I suppose one could also add or subtract an offset to adjust the time for clock drift too, but that seems like a hard way to set the clock.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: December 16,2009

    Created by: jonesjeremya

    Maybe i'm looking at this the wrong way, but can't you just make a clock in the ladder using time bits to increment a register? Say, in military format with a reset on the register(s) at midnight? In that way you can adjust the time from the HMI and the daylight savings can be toggled when needed at the appropriate times in the year. I don't know how accurate the time would be over an extended length of time?

    Can it be done through the ladder?

    How accurate would it be over time?

    Sorry, I have not done applications that are based on time, so I do not know first hand, but my idea seems conceivable, to me.

    Jeremy

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: December 16,2009

    Created by: bfitz

    Read-only RTC registers are common, the DL series is the same way. In the DL series, if you want to change the clock you have to use the TIME instruction (or DATE for calendar changes), plus a couple of specifically formatted registers. I don't have the Click software installed, but check it for a TIME instruction.

    Brian

  • adccommunitymod (AutomationDirect)

    Created Date: December 17,2009

    Created by: BAK96

    Unfortunately there is no time or clock instruction for the ladder. The clock features are under PLC Calendar/Clock setup. You set the time & date from

    the PC or manualy select a date & time. Then write to the PLC.

    Would be nice if you could adjust through the ladder via HMI.

  • adccommunitymod (AutomationDirect)

    Created Date: December 17,2009

    Created by: Dan @ CHP

    Thanks for all the interest. I do like the idea of using two counters for the clock; I 've long been a fan of using counters for long duration timers.

  • adccommunitymod (AutomationDirect)

    Created Date: December 19,2009

    Created by: DetroitSound

    Thanks for all the interest. I do like the idea of using two counters for the clock; I 've long been a fan of using counters for long duration timers.

    You 've mentioned that before and it was something I never even thought of - a timer is a timer; a counter is a counter and never the twain shall meet,right? Wrong. But it has proven to be a great way of doing it. I thank you.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: December 19,2009

    Created by: Rich19551

    You 've mentioned that before and it was something I never even thought of - a timer is a timer; a counter is a counter and never the twain shall meet,right? Wrong. But it has proven to be a great way of doing it. I thank you.

    With all the talk about clocks I thought I would try something different. I haven't tried it but it should work. Don't know it would work with Click (I would have to read up on it).

    PLC 05

    // Rung 1

    // Address 0

    STR SP1

    STR C0

    TMRA T0 K600

    // Rung 2

    // Address 5

    STR T0

    PD C0

    // Rung 3

    // Address 7

    STR C0

    INC V2000

    // Rung 4

    // Address 10

    STRE V2000 K60

    INC V2002

    LD K0

    OUT V2000

    // Rung 5

    // Address 16

    STRE V2002 K24

    LD K0

    OUT V2002

    // Rung 6

    // Address 20

    END

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: December 16,2009

    Created by: Dan @ CHP

    Is there a way to adjust the Click PLC clock and calendar from the operating program? I'm installing this PLC as a heating control in a school and would like to give the custodian the ability to reset the clock from the C-more Micro HMI. I also have an automatic Daylight Saving Time routine I'd like to use.

  • leo (Customer)

    HI

    You can change the time and date from the hmi. I am doing it on a machine, I believe sd registers sd 34,35 36 are read/write

  • leo (Customer)

    I believe there is am explation how to do it in the help file,

    look under changeing date and time without click program