adccommunitymod (AutomationDirect) asked a question.

Click and thermocouple

Created Date: July 19,2012

Created By: bluegoose

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Can a click be used to monitor only water temps?


  • adccommunitymod (AutomationDirect)

    Created Date: July 19,2012

    Created by: Adisharr

    The click doesn't have any thermocouple I/O at this time, you might be better off looking at a DL05/06 with a TC card.

    Here's a 4 point Thermocouple card for the DL 05/06 series.

    http://www.automationdirect.com/adc/Shopping/Catalog/Programmable_Controllers/DirectLogic_Series_PLCs_%28Micro_to_Small,_Brick_-a-_Modular%29/DirectLogic_05_%28Micro_Brick_PLC%29/Analog_I-z-O/F0-04THM

    I think you can do 12 points with a DL06 (haven't looked to see if the DL06 bus can power three of them)

    DL05 is limited to 4 (only one slot)

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: July 19,2012

    Created by: Tinker

    One option if you only need to monitor one or two thermocouples could be to use a SOLO temperature controler as an interface and use one of the CLICKs with RS485 to retrive the PV from the SOLO via modbus. A SOLO costs around $100 and the F0-04THM $201, if you need all four chanels of a F0-04THM then it would probably be more cost effective (supposing you already have DirectSoft or your progect doesn't need more than a hundred instructions) but for one channel not so much.

    Another option for "water temps " (assumning liqid water at anything like normal pressure) would be to use one of the TTD series of temperature transmiters conected to the 4-20mA input(s) of an analog CLICK, the price would be similar to a SOLO but programing would be eaiser.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: July 20,2012

    Created by: bluegoose

    I am looking at using temp transmitters rather than thermocouples. AD has some that are cose effective with 4-20ma out. The click has a CPU with analog in options. I only need two channels so that should work ok.

  • adccommunitymod (AutomationDirect)

    Created Date: July 19,2012

    Created by: bluegoose

    Can a click be used to monitor only water temps?