adccommunitymod (AutomationDirect) asked a question.

Can I use a spare PLC unit as an I/O module?

Created Date: January 10,2013

Created By: brent14

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

In the project I am working on, I have: 1 - C0-02DR-D PLC 7 - C0-08TR I/O Modules 1 - C0-01DR-D Unused PLC I need more outputs for my system, I know I have room for 1 more of the C0-08TR, but I have a PLC just sitting around which I would like to use. Is there any way of wiring these together to make it act as a I/O Module?


  • adccommunitymod (AutomationDirect)

    Created Date: January 10,2013

    Created by: ADC_CommTeam02

    The only option is to talk to the other Click plc via the RS232 or RS485 ports, read the I/O into the C0-02DR-D and then use this in your programming logic.

    I would recommend buying another C0-08TR.

  • adccommunitymod (AutomationDirect)

    Created Date: January 19,2013

    Created by: Adisharr

    Trying to expand I/O serially is a complete waste of time since you have room for another module unless you just want to play around with it.

  • adccommunitymod (AutomationDirect)

    Created Date: January 28,2013

    Created by: brent14

    Thanks for the advice!

    And I just bought another one, I was just looking to save a quick buck and was wondering if it would be easy to do.

  • adccommunitymod (AutomationDirect)

    Created Date: January 10,2013

    Created by: brent14

    In the project I am working on, I have:

    1 - C0-02DR-D PLC

    7 - C0-08TR I/O Modules

    1 - C0-01DR-D Unused PLC

    I need more outputs for my system, I know I have room for 1 more of the C0-08TR, but I have a PLC just sitting around which I would like to use.

    Is there any way of wiring these together to make it act as a I/O Module?

    Expand Post