adccommunitymod (AutomationDirect) asked a question.
click c000dd20 with 6 c016td2
Created Date: March 15,2014
Created By: agrevel
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
Hi all I have a click plc that does not seem to how that the additional outputs are there (the green leds are on)any ideas
Created Date: March 18,2014
Created by: OpZed
You added the modules to the System Configuration screen and then downloaded the new project into the PLC? The System Configuration also shows you the correct Output Addresses for each module. Be sure to notice that the first digit (hundreds position) represents the Slot number. Y001 is Slot 0 (on-board), Y101 is Slot 1, Y201 is Slot 2 ...
Created Date: March 22,2014
Created by: agrevel
thanks
thanks I found it I would have though it auto config
Created Date: March 15,2014
Created by: agrevel
Hi all I have a click plc that does not seem to how that the additional outputs are there (the green leds are on)any ideas