adccommunitymod (AutomationDirect) asked a question.
Do I want to use 16 bit signed or 16 bit Unipolar for an analog module input?
Created Date: July 16,2019
Created By: xtal_01
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
Here I go reading again ... I see the analog input module can be set up as signed -32767 to 32767 ... which really does not make sense to me as 4-20 mA is always going to be positive and the WX range says 0-32767 Or do I want to enable 16 bid unipolar which gives me 0-32767 ? Or does this even matter as I am letting the PLC scale WX from ??? to RX (0-250)? Thanks again .... Mike
Created Date: July 16,2019
Created by: xtal_01
Here I go reading again ... I see the analog input module can be set up as signed -32767 to 32767 ... which really does not make sense to me as 4-20 mA is always going to be positive and the WX range says 0-32767
Or do I want to enable 16 bid unipolar which gives me 0-32767 ?
Or does this even matter as I am letting the PLC scale WX from ??? to RX (0-250)?
Thanks again .... Mike
Created Date: July 16,2019
Created by: BobO
If you have the PLC scaling it there is nothing more for you to do.
Created Date: July 16,2019
Created by: xtal_01
You are the man ... so in this case since I am scaling, there will be no difference in accuracy or ??? no matter which I choose.
If there is a short answer ... why or when would you choose one over the other?
I know ... way tooooo may questions ... I just like to know why I do things.
Thanks .... Mike
Created Date: July 17,2019
Created by: BobO
I seriously doubt that the difference between 15 and 16 bits will make a meaningful difference in a flow integrator.
Created Date: July 17,2019
Created by: genebond
You are the man ... so in this case since I am scaling, there will be no difference in accuracy or ??? no matter which I choose.
If there is a short answer ... why or when would you choose one over the other?
I know ... way tooooo may questions ... I just like to know why I do things.
Thanks .... Mike
On one transducer, the range may be 0 to 150psi for example, so Unsigned is fine. But, on another, the range may be -30 to 100 psi, so Signed may be more appropriate.