I have a DirectLogic 205 processor which I do NOT have the program for. I have never been online with a DirectLogix 205 before. Been online only with the DoMore & Click PLC's. What I am looking to do, is make some program changes and also get this PLC rack on out plant ethernet network. I can figure out how to get online with it. My bigger question, is looking for the best way to get this on Ethernet. I found the ethernet processor, but I am out of slots. Looks like I could buy a higher density Analog card, and free up a slot. Is this my best approach? What are my options?
Created Date: October 18,2017
Created by: dslusser
I have a DirectLogic 205 processor which I do NOT have the program for. I have never been online with a DirectLogix 205 before. Been online only with the DoMore & Click PLC's. What I am looking to do, is make some program changes and also get this PLC rack on out plant ethernet network. I can figure out how to get online with it. My bigger question, is looking for the best way to get this on Ethernet. I found the ethernet processor, but I am out of slots. Looks like I could buy a higher density Analog card, and free up a slot. Is this my best approach? What are my options?
Created Date: October 18,2017
Created by: dslusser
Sorry, forgot to post the Image: http://tinypic.com/r/2w23sbc/9
Created Date: October 18,2017
Created by: winterrossi
Buy a Do More processor and change it. The Do More software has a migration tool for DL programs.
Created Date: October 18,2017
Created by: commander
The migration tool from DL to Do-More does not convert everything and if you have a large program I would not recommend it. You can try the Do-More software and do the conversion to see if that looks like something you want to reprogram.
I could not get the image to work. Yes, make room for the ethernet card module or buy a bigger rack if your panel has the room.
Created Date: October 18,2017
Created by: bcarlton
It's pretty obvious from the picture that your enclosure could not hold a longer rack even if one existed (it doesn't, that's the longest rack). So your choices are change to the Do-more processor (with the program re-write) or change to a higher density I/O card (like the analog you suggest) to free up a space for the ECOM100.
Created Date: October 18,2017
Created by: dslusser
I didn't know you could swap the Direct Logic for a Do-More. Of course, I knew the footprints were the same, just didn't know it would logcally work.
So if I upgrade to something like this - H2-DM1E , and also convert the program, I should be good to go.
I will have to take a look at the program and see how bad it is in case the convert doesn't work that well.
Created Date: October 18,2017
Created by: bcarlton
Remember that Do-more has a simulator so you may be able to test the code before you go for it.
Created Date: October 18,2017
Created by: BobO
The program migration tool might convert 100% or 10%...depends greatly on the program. DL and Do-more instruction sets are similar in some ways and different in others. Best thing to do is to suck out the DL program, export from DSP, then import into Do-more Designer and see what you get.
If the program is mostly ladders, it converts well. Math may or may not depending on how it was written, but Do-more is vastly more capable than DL, so everything can be translated.
And if you have questions, several Host guys frequent the forum and are more than happy to help.
Created Date: October 19,2017
Created by: winterrossi
I didn't know you could swap the Direct Logic for a Do-More. Of course, I knew the footprints were the same, just didn't know it would logcally work.
So if I upgrade to something like this - H2-DM1E , and also convert the program, I should be good to go.
I will have to take a look at the program and see how bad it is in case the convert doesn't work that well.
I would think with as much analog as you have there's gonna be quite a few things that you'll have to rewrite. The upside to that is Do More analog is very simple to program, unlike DL.