adccommunitymod (AutomationDirect) asked a question.
Connect to DoMore on network
Created Date: March 16,2017
Created By: jtak101
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I have a DoMORE PLC, gave a static IP address to the DoMore. Its connected on our work network, I have the email function working, but wanted to know how I could go about getting online with the PLC without having to walk my laptop over and plug into the USB. Thanks,
Created Date: March 16,2017
Created by: jtak101
I have a DoMORE PLC, gave a static IP address to the DoMore. Its connected on our work network, I have the email function working, but wanted to know how I could go about getting online with the PLC without having to walk my laptop over and plug into the USB.
Thanks,
Created Date: March 16,2017
Created by: mwdkmpr
It is easy if your computer is on the same subnet as the PLC. Create a new Ethernet link in DMD using the IP that you gave the PLC.
Created Date: March 16,2017
Created by: jtak101
It is easy if your computer is on the same subnet as the PLC. Create a new Ethernet link in DMD using the IP that you gave the PLC.
Got it thanks for the help... that was easy.
Created Date: March 17,2017
Created by: jtak101
It is easy if your computer is on the same subnet as the PLC. Create a new Ethernet link in DMD using the IP that you gave the PLC.
Had a follow up question, I did get it working but do you leave the PLC switch in Terminal Mode or Run mode, when I connected got a message saying PLC not in term. mode not all functions will be available, I have the PLC in Run mode.
Thanks,
Created Date: March 17,2017
Created by: BobO
Had a follow up question, I did get it working but do you leave the PLC switch in Terminal Mode or Run mode, when I connected got a message saying PLC not in term. mode not all functions will be available, I have the PLC in Run mode.
Thanks,
When the switch is in RUN, DmD cannot change to program mode, which is required for certain operations. While programming, leave it in TERM. When commissioned, either is fine.
Created Date: March 17,2017
Created by: jtak101
When the switch is in RUN, DmD cannot change to program mode, which is required for certain operations. While programming, leave it in TERM. When commissioned, either is fine.
got it thanks!