adccommunitymod (AutomationDirect) asked a question.

P2-HSI Counting Issues

Created Date: October 15,2019

Created By: robertkeenan

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a P2000 PLC controlling 5 conveyors operated by drives. Each of the conveyors has a quadrature shaft encoder on the conveyor which I am hoping to use for keeping the conveyors in sequence. The problem I have is that if I run anyone of the motors all the counters change in value. To help fault find I removed all the field wiring from the cards and then run one of the motors. They stayed at zero which seem to indicate an issue with the wiring picking up noise. However after a few minutes one of the counters jumped to a very large number, 536870912, while all the other counters stayed at zero. Reset the counters a few times and only one of them changes to that number. If I wait a few more minutes that number will double, 1073741824, and then it doubles again to 2147483647. It has now appeared to stop increasing and all my other cards are still at zero. Have I got a wiring issue or a software issue or a hardware issue?


  • adccommunitymod (AutomationDirect)

    Created Date: October 15,2019

    Created by: robertkeenan

    I have a P2000 PLC controlling 5 conveyors operated by drives. Each of the conveyors has a quadrature shaft encoder on the conveyor which I am hoping to use for keeping the conveyors in sequence. The problem I have is that if I run anyone of the motors all the counters change in value. To help fault find I removed all the field wiring from the cards and then run one of the motors. They stayed at zero which seem to indicate an issue with the wiring picking up noise. However after a few minutes one of the counters jumped to a very large number, 536870912, while all the other counters stayed at zero. Reset the counters a few times and only one of them changes to that number. If I wait a few more minutes that number will double, 1073741824, and then it doubles again to 2147483647. It has now appeared to stop increasing and all my other cards are still at zero. Have I got a wiring issue or a software issue or a hardware issue?

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 15,2019

    Created by: bsinkovich

    Show picture of how you got the system wired. What drives?

  • adccommunitymod (AutomationDirect)

    Created Date: October 15,2019

    Created by: MikeN

    Just to confirm, you are using a separate inpuit channel for each quadrature encoder right? Which should mean you have 3 HSI cards for the 5 encoders?

    Since this should mean you have a spare channel open, could you try switching the wiring from the "bad channel " onto the spare and see if the behavior is the same?

  • adccommunitymod (AutomationDirect)

    Created Date: October 15,2019

    Created by: robertkeenan

    What I have just done is set the spare channel with some parameters for Count, Velocity and Reset. Since doing that all the counters keep their zero value. This has run for an hour with no issues. Rewired the encoders back into the 5 channels and now they are all counting again. Will order some new cable for the encoders as this is an old panel which is being upgraded to the new PLC.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 15,2019

    Created by: MikeN

    What I have just done is set the spare channel with some parameters for Count, Velocity and Reset. Since doing that all the counters keep their zero value. This has run for an hour with no issues. Rewired the encoders back into the 5 channels and now they are all counting again. Will order some new cable for the encoders as this is an old panel which is being upgraded to the new PLC.

    Was the channel that was acting funny on the same module as the spare that wasnt set up for anything before?

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 15,2019

    Created by: robertkeenan

    The funny channel is on a different card from the spare one. Should unused channels be connected to ground.

  • adccommunitymod (AutomationDirect)

    Created Date: October 15,2019

    Created by: MikeN

    I dont think so. I have never connected them to ground before.

  • adccommunitymod (AutomationDirect)

    Created Date: October 16,2019

    Created by: robertkeenan

    I have now found some good screened cable and wired up the first two encoders on card one. They appear to be working and counting proper values. Still concerned about why the other encoder positions which have no field wires in them yet are still counting. Maybe once I get more cable and wire them up this problem will be fixed but in the future how will I know it is a count and not a random number.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: November 04,2019

    Created by: robertkeenan

    Eventually the cable arrived and I now have wired up all 5 encoders with screened encoder cable and it is earthed at the encoder end. When I run one of the motors all the other encoders will produce random counts. It is most noticeable when the motor is stopped. The counting will accelerate while the drive is slowing down and produce some extremely large numbers. The PLC is controlling the drives over the network so it does not have any direct connection to the drive. The drives are at least a meter from the PLC and the cabling is going out on different sides of the panel. I am starting to think that these P2-HSI cards are very sensitive to noise and was thinking of wiring the encoders to ordinary PLC inputs. This will give me a counter but I might have to live with the fact that it is not a directional counter. Has anyone written a bit of ladder logic which would allow the encoders to count along with being directional. The speed it counts at will not be an issue.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: November 04,2019

    Created by: dnj

    I suggest you go online with the cpu and create a system report so we can see how you have the system configured. In addition, please provide pics of your wiring from the HSI to ZL-RTB40, encoder wiring and cabinet.

10 of 17