adccommunitymod (AutomationDirect) asked a question.

ControlLogix Lxx using Productivity 3000 I/O

Created Date: December 07,2018

Created By: cra_fizzer

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

What is the best way to have a ControlLogix processor talk to P3000 I/O? The system currently has a main rack w/ a P3-550 CPU. It is talking to several racks via P3-RX I/O adapters. It is also talking to GS2 drives via GS-EDRV100 modules. The Client mandates the ControlLogix processor. Existing I/O is OK to keep using. Do the RX scanners talk Modbus TCP? I'm thinking a HMS Anybus adapter would work if that is the case. If they don't, do I use the 550 CPU as an Ethernet/IP adapter and map the I/O? Thanks, Tony


  • adccommunitymod (AutomationDirect)

    Created Date: December 07,2018

    Created by: cra_fizzer

    What is the best way to have a ControlLogix processor talk to P3000 I/O? The system currently has a main rack w/ a P3-550 CPU. It is talking to several racks via P3-RX I/O adapters. It is also talking to GS2 drives via GS-EDRV100 modules. The Client mandates the ControlLogix processor. Existing I/O is OK to keep using.

    Do the RX scanners talk Modbus TCP? I'm thinking a HMS Anybus adapter would work if that is the case.

    If they don't, do I use the 550 CPU as an Ethernet/IP adapter and map the I/O?

    Thanks,

    Tony

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: December 07,2018

    Created by: g.mccormick

    I would use the 550 as ethernetip adapter to the ab.