P2000 and Mitsubishi GOT1000 via Modbus TCP

Created Date: October 20,2016

Created By: bobby5184

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hello, Using the P2-550 PLC and trying to connect a Mitsubishi GT1455HS-QTBDE HMI via Modbus TCP. I have been working with my Mitsubishi rep and I believe I have everything set correctly in the HMI. In the Productivity Programming Suite under hardware config I click on the ethernet ports tab and verify my IP and Subnet are good. Is there anything else I need to do to get Modbus TCP funtional? I can go online and load a program via the ethernet port no problem


  • adccommunitymod (AutomationDirect)

    Created Date: October 20,2016

    Created by: bobby5184

    Hello, Using the P2-550 PLC and trying to connect a Mitsubishi GT1455HS-QTBDE HMI via Modbus TCP. I have been working with my Mitsubishi rep and I believe I have everything set correctly in the HMI. In the Productivity Programming Suite under hardware config I click on the ethernet ports tab and verify my IP and Subnet are good.

    Is there anything else I need to do to get Modbus TCP funtional? I can go online and load a program via the ethernet port no problem

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 20,2016

    Created by: ADC_CommTeam02

    You will need to go into the Tag Database and assign Modbus addresses (see attached .jpg) to any tag that the HMI will be trying to access. The P2 then will be the slave to your mastering HMI device.