adccommunitymod (AutomationDirect) asked a question.
Created Date: October 20,2016
Created By: bobby5184
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
Hello, Using the P2-550 PLC and trying to connect a Mitsubishi GT1455HS-QTBDE HMI via Modbus TCP. I have been working with my Mitsubishi rep and I believe I have everything set correctly in the HMI. In the Productivity Programming Suite under hardware config I click on the ethernet ports tab and verify my IP and Subnet are good. Is there anything else I need to do to get Modbus TCP funtional? I can go online and load a program via the ethernet port no problem
Created Date: October 20,2016
Created by: bobby5184
Hello, Using the P2-550 PLC and trying to connect a Mitsubishi GT1455HS-QTBDE HMI via Modbus TCP. I have been working with my Mitsubishi rep and I believe I have everything set correctly in the HMI. In the Productivity Programming Suite under hardware config I click on the ethernet ports tab and verify my IP and Subnet are good.
Is there anything else I need to do to get Modbus TCP funtional? I can go online and load a program via the ethernet port no problem
Created Date: October 20,2016
Created by: ADC_CommTeam02
You will need to go into the Tag Database and assign Modbus addresses (see attached .jpg) to any tag that the HMI will be trying to access. The P2 then will be the slave to your mastering HMI device.