adccommunitymod (AutomationDirect) asked a question.

P3-08AD card simulation

Created Date: April 10,2014

Created By: jparker

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a P3-08AD card that I 've set up in the software for 0-20mA. I have the Ziplink ZL-RTB20 wired correctly. I have no errors on the LCD. In data view the under range flag is checked because I can't see any 4-20 sensor input. If I set the card up for 0-10 or any other voltage I read fine. I am trying to source a 4-20mA signal to ch1 from a Fluke 744 process meter. If I take 24vdc + to I1 and then the positive lead from the meter to I1 and the negative to -24 I can't read anything. I think I should see the sourced current on I1. What am I doing wrong?? Any Ideas why I can't read current on this card? Much appreciate any thoughts Thanks


  • adccommunitymod (AutomationDirect)

    Created Date: April 10,2014

    Created by: bcarlton

    As shown on page 49 of the meter's manual

    Connect meter red lead to the +24 volt supply

    Connect meter black lead to the I1+ input

    Jumper I1+ to V1+

    Use the 'simulate transmitter ' function on the meter.

    You should be able to regulate current into the first channel and see its reading from within the software.

    Note: change the '1 ' in the above terminal names to whichever input your are testing.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: April 10,2014

    Created by: jparker

    Thanks, the problem was that I was jumpering I+ to 24vdc. I needed to jump I+ to V1+

    The manual that comes with the card is not real clear on that. Thank you

  • adccommunitymod (AutomationDirect)

    Created Date: April 10,2014

    Created by: jparker

    I have a P3-08AD card that I 've set up in the software for 0-20mA.

    I have the Ziplink ZL-RTB20 wired correctly. I have no errors on the LCD. In data view the under range flag is checked because I can't see any 4-20 sensor input. If I set the card up for 0-10 or any other voltage I read fine.

    I am trying to source a 4-20mA signal to ch1 from a Fluke 744 process meter. If I take 24vdc + to I1 and then the positive lead from the meter to I1 and the negative to -24 I can't read anything. I think I should see the sourced current on I1. What am I doing wrong?? Any Ideas why I can't read current on this card? Much appreciate any thoughts

    Thanks