I'm sure I'm missing something incredibly obvious, but I'm not seeing it, so it's time to reach out: I have a P2-550 CPU talking to a GS1 VFD over RS485. I'm able to read registers from the VFD and load commands to it (e.g., set a frequency, change the run command bit from 0 to 1). I'm showing zero communication faults in my ladder, so I know they 're talking well. The problem is that even though I see a valid run command on the VFD (9.27), the VFD doesn't actually start, and the run LED on the display never turns on. My other settings are: 3.00: 4 and 4.00: 5. I 've also disabled any transmission fault handling on the VFD, just in case that was interfering. Any ideas?
Created Date: September 03,2016
Created by: Frontier
I'm sure I'm missing something incredibly obvious, but I'm not seeing it, so it's time to reach out:
I have a P2-550 CPU talking to a GS1 VFD over RS485. I'm able to read registers from the VFD and load commands to it (e.g., set a frequency, change the run command bit from 0 to 1). I'm showing zero communication faults in my ladder, so I know they 're talking well. The problem is that even though I see a valid run command on the VFD (9.27), the VFD doesn't actually start, and the run LED on the display never turns on. My other settings are: 3.00: 4 and 4.00: 5. I 've also disabled any transmission fault handling on the VFD, just in case that was interfering.
Any ideas?
Created Date: September 04,2016
Created by: Frontier
Here's my settings. Again, I can communicate with the VFD, but it just doesn't go into Run mode.
P3.00: 04
P4.00: 05
P9.00: 2 (PLC is 1)
P9.01: 19.2k
P9.02: 5
Created Date: September 04,2016
Created by: Ridgeline Mach
Can you post your ladder code? I 've already done this on three projects, but to GS2 and 3 drives, so it might help us. But for now, for example with what I did, I used a simple timer, with a preset of 1, pulse a counter set to 5, and used a compare value of the counters current value, to trigger Modbus read/writes so they did not read/write simultaneously. Another thing I notice when things are working well (and I used the terminal serial port), I'll see the TX and RX lights blinking back and forth happily (when I had problems, only TX would blink).
- Todd
Created Date: September 04,2016
Created by: Frontier
Ladder attached. I don't think I have a communication problem, as my TX and RX lights are blinking happily, and I can see the set frequency change on the VFD display.
n102556
Created Date: September 04,2016
Created by: Frontier
All right, got it figured out!
In the manual, there's a note on page 4-51 that says "Do not attempt to both Run and Jog (P9.27 & P9.31) in one Modbus write command. ". There seems to be a typo here, so it should actually say "Do not attempt to send both Run and Jog (P9.27 & P9.31) in one Modbus write command. ". It doesn't matter if you 're only sending a zero to the jog register; the VFD doesn't want to see the register written into in the same modbus write session. The fix for my ladder above is to thange the MWX command in rung 2 to start at array index 1 and end at 5, skipping the jog entirely.
Weird, but at least I figured it out. Thanks everyone for helping me look for this.
Created Date: September 04,2016
Created by: kewakl
Thanks for that, frontier
Created Date: September 04,2016
Created by: Mike Nash
Weird, but at least I figured it out.
I sure wouldn't have interpreted it that way either. Good job. I did take a look at the manual earlier but saw nothing helpful to offer.
Created Date: September 05,2016
Created by: Frontier
The weird thing is the GS2 manual is almost identical to the GS1 manual, but this note is left out completely... There might be more going on in the firmware than I thought...
Created Date: September 05,2016
Created by: Ridgeline Mach
Well, I learned something new today. My first use of this was in a Click 5-years ago. Looking at your code taught me that poll timing is built into Modbus commands of the Productivity Suite. Who-da thunk...