Does anyone know if events can be turned on and off by the operator using a tag?
Created Date: March 11,2020
Created by: Glen Walker
Does anyone know if events can be turned on and off by the operator using a tag?
Created Date: March 11,2020
Created by: Garry
Yes, events can be triggered by a tag.
https://www.automationdirect.com/mic...ontent/136.htm
Do you have a specific example that is not working?
Regards,
Garry
Created Date: March 11,2020
Created by: Glen Walker
I think I should clarify. I was trying to find out if Events can be Enabled/Disabled by the Operator using a tag?
Created Date: March 12,2020
Created by: sii
You can set any particular event to be conditioned upon multiple tags. Say for example you have an event based upon a tag in your plc, simply add a second tag, internal to your hmi that must be on to trigger the event. Alternatively the enable tag could be located in the plc.
Created Date: March 12,2020
Created by: ewitcher
Yes, when you add the event, set No. of Tags: to 2 and then select the appropriate logic needed.
{ "data-align ": "none ", "data-size ": "large ", "data-attachmentid ":129323}
Created Date: March 13,2020
Created by: Glen Walker
Thanks Guys, Good idea! Im working on a cookie cutter application that will be sold as a package and the end user needs to have the ability to disable events depending on their specific setup.
Thanks again