Hi, I’m looking to switch a tag value on the c-more upon listening for a tag value on my do-more plc. Is this possible?


  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2020

    Created by: PembyBroche

    Hi, I’m looking to switch a tag value on the c-more upon listening for a tag value on my do-more plc. Is this possible?

  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2020

    Created by: bcarlton

    It's unclear what you want to do. Can you give a specific example?

  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2020

    Created by: kewakl

    It sounds like you need to look at the Event Manager in CMore.

    Only available in C-More EA7 or EA9.

    If you have a Micro, it cannot do it.

    As bernie says, your request is unclear. Please provide more info about what you need to accomplish.

  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2020

    Created by: PembyBroche

    Apologies! I have a button on the the c-more that toggles a discrete tag MC1 on. When this happens, my PLC runs a subroutine and outputs Y0 on. I’m trying to toggle MC1 off when I see that Y0 is on.

  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2020

    Created by: kewakl

    Which CMore family?

    Is the PLC a DoMore BRX?

  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2020

    Created by: PembyBroche

    I'm using an EA3 panel (EA3-T4CL). I am using a DoMore BRX (BX-DM1E-18ED23-D)

  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2020

    Created by: kewakl

    EA3 does not support events, so you should consider doing this in the BRX

  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2020

    Created by: kewakl

    . Y0 MC1

    .-----]^

    I don't know if DoMore supports turning off MC bits from its own code. The -]^ is a rising edge.

  • adccommunitymod (AutomationDirect)

    Created Date: February 23,2020

    Created by: franji1

    I don't know if DoMore supports turning off MC bits from its own code. The -]^ is a rising edge.

    It does - what you have should work.

  • adccommunitymod (AutomationDirect)

    Created Date: February 24,2020

    Created by: PembyBroche

    . Y0 MC1

    .-----]^

    I don't know if DoMore supports turning off MC bits from its own code. The -]^ is a rising edge.

    This has resolved my issue. Thank you so much for helping me!