adccommunitymod (AutomationDirect) asked a question.

Timeout messages

Created Date: May 14,2019

Created By: Ryan_Poethke

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

On the EA9 panels, is there a way to suppress the PLC COMs timeout messages that pop up at the top of the screen? I have an application where I may or may not have the panel connected to multiple PLCs over Ethernet, and I don't want to see those error messages all the time. I'm handling COM's timeout issues and reporting in a PLC that will always be present on the network with the HMI, and reporting to the HMI appropriately. Thanks, Ryan Poethke


  • adccommunitymod (AutomationDirect)

    Created Date: May 14,2019

    Created by: Ryan_Poethke

    On the EA9 panels, is there a way to suppress the PLC COMs timeout messages that pop up at the top of the screen? I have an application where I may or may not have the panel connected to multiple PLCs over Ethernet, and I don't want to see those error messages all the time. I'm handling COM's timeout issues and reporting in a PLC that will always be present on the network with the HMI, and reporting to the HMI appropriately.

    Thanks,

    Ryan Poethke

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: May 14,2019

    Created by: Do-more PE

    See the software help topic CM525.

  • adccommunitymod (AutomationDirect)

    Created Date: May 14,2019

    Created by: Ryan_Poethke

    See the software help topic CM525.

    That does the trick. Thanks!

    Ryan Poethke

  • adccommunitymod (AutomationDirect)

    Created Date: May 15,2019

    Created by: TheGreatMarklar

    A related question: is there a way to suppress the alarm banners at the top of the screen?

  • adccommunitymod (AutomationDirect)

    Created Date: May 16,2019

    Created by: Do-more PE

    Not at this time.