adccommunitymod (AutomationDirect) asked a question.
Daylight Savings Time with DL06 and EA9 HMI
Created Date: March 20,2019
Created By: bergmw
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
Does anyone have a fix for syncing the clocks of the DL06 and EA9? What a headache in a busy shop, not to mention the clocks don't keep equal time. Hoping to have the HMI sync to the PLC. Any suggestions would be greatly appreciated.
Created Date: March 20,2019
Created by: bergmw
Does anyone have a fix for syncing the clocks of the DL06 and EA9? What a headache in a busy shop, not to mention the clocks don't keep equal time.
Hoping to have the HMI sync to the PLC. Any suggestions would be greatly appreciated.
Created Date: March 29,2019
Created by: AlecTek
C-more software -> Setup -> Clock Cource
Created Date: April 03,2019
Created by: RoloTomassi
https://support.automationdirect.com/examples.html
Automation Direct also has an example for have the PLC manage its own clock adjustment for Daylight Savings Time. The DL06 is included in the applicable CPU’s. The link is posted above. It’s the very first one under General Examples.