adccommunitymod (AutomationDirect) asked a question.
Created Date: March 23,2018
Created By: dbanks
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
AD's Prod Suite 2k. P2-550. SMVector VFD We'll be utilizing digital I/O for communications. I 'ev set it up within the SMV. I'm just a bit of a loss for how to write it in the PLC. I know it's scaled but I can't figure out what the range is. I feel like I saw 0-16535 somewhere, but can't find a source to corroborate at this point. It'll be 0-100 on the HMI/PLC if that's of relevance. If it's digital IO, how am I sending anything specific? I want to be able to set a speed from 0-100% on the HMI-have it go through the PLC-go through the VFD-output frequency corresponding to the input. Any advice out there? I 've attached the manuals I 've been on. Other hardware we 're utilizing: P208AD-1 p204da https://www.promelec.ru/pdf/SV01C-e1.pdf https://cdn.automationdirect.com/static/manuals/p2userm/p2userm.pdf Yes, I am a bit lost here.
Created Date: March 23,2018
Created by: dbanks
AD's Prod Suite 2k. P2-550.
SMVector VFD We'll be utilizing digital I/O for communications. I 'ev set it up within the SMV. I'm just a bit of a loss for how to write it in the PLC. I know it's scaled but I can't figure out what the range is. I feel like I saw 0-16535 somewhere, but can't find a source to corroborate at this point. It'll be 0-100 on the HMI/PLC if that's of relevance.
If it's digital IO, how am I sending anything specific? I want to be able to set a speed from 0-100% on the HMI-have it go through the PLC-go through the VFD-output frequency corresponding to the input. Any advice out there? I 've attached the manuals I 've been on. Other hardware we 're utilizing:
P208AD-1
p204da
https://www.promelec.ru/pdf/SV01C-e1.pdf
https://cdn.automationdirect.com/static/manuals/p2userm/p2userm.pdf
Yes, I am a bit lost here.
Created Date: March 24,2018
Created by: Ridgeline Mach
You can't use "digital I/O " to set a speed from 0-100%. You'll need an analog output module connected to the analog input of your VFD to get 0-100% adjustability.
Created Date: March 24,2018
Created by: Ridgeline Mach
Another way you can control the drive is serially. I 've done it using Modbus RTU read/writes to a Yaskawa drive from the RS485 port on the P2K's CPU. Controlling it this way, you won't need to use the digital I/O. You can do forward, reverse, run, and speed via writes, and with reads, get the amperage reading, and faults from the drive. Not familiar with Lenze, but maybe this manual will help.
http://download.lenze.com/TD/ESV__SMV%20Modbus%20module__v3-0__EN.pdf
Created Date: March 24,2018
Created by: johnaden
If you only need a few specific speeds, Digital Outputs could control the VFD to command some Preset Speeds.
Created Date: March 28,2018
Created by: brucekess
looks like the analog out is 65535 for highest count. So your scale would look like, on a Do More which is what i use, not sure what a p2000 scale instruction looks like. but the V0 would be your (input) memory location from the HMI. and the V1 would be the output (memory location ) of the SCALE instruction. Then you can MOVE V1 to the address of the analog output or maybe just put the analog output in place of V1. Again i don't use the p2000 so i'm not sure what the scale command looks like but essentially it should be similar to this. Looking at the Technical Specs of the analog card, it says its unipolor 65535 or bipolar -32768 - +32767. if your using 4 - 20 ma output you would have to change the scaled min to what ever 4 ma is. Sometimes you can find examples in the manual that give you this number.
input: V0
Scale min: 0
Scale max: 100
Scaled min: 0
Scaled max: 65535
Output: V1
and if you want you can make V0 a R0 and use 0.0 min and 100.0 max and you get a bit more out of the speed range by using decimal numbers. 55.6% speed vs 55 or 56% depending on rounding.