How to connect a BX-DM1-18ER-D PLC to C-more using an EA7-T6C hmi display
Created Date: November 10,2017
Created By: gersonm
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
My PLC does not have the modem cable port to connect to. Is this possible? The modem cable has 6 connections but my PLC only has 3 connections for RS232/485.
Created Date: November 10,2017
Created by: gersonm
My PLC does not have the modem cable port to connect to. Is this possible? The modem cable has 6 connections but my PLC only has 3 connections for RS232/485.
Created Date: November 10,2017
Created by: kewakl
Look on the back of the CMore. You should see a 15-pin connector. Two of those pins should match up to two of the pins on your DoMore.
Depending on whether you choose RS232 or RS485, you would select a different pair on the CMore.
The same two pins would be used on DoMore regardless of RS232 or RS485 selection. Software Selection.
I have NOT made this connection, so I cannot 100% confirm.
CMORE spec sheet https://cdn.automationdirect.com/sta...inch_12_09.pdf Page E10-42
DoMore spec sheet https://cdn.automationdirect.com/sta...xdm1_18erd.pdf Page BRX-45
EDIT: A POM module is about $70. Maybe BobO or someone else can confirm that the ethernet POM will work for CMore comms.
Created Date: November 10,2017
Created by: Do-more PE
The Ethernet POM should work fine for communications to a C-more as would the RJ12 POM.
Created Date: December 14,2017
Created by: Mike Nash
So where are the cables for C-more/C-more Micro to Do-more 3 terminal Serial Port? There's not even a connection diagram for the Do-more in the C-more Micro Manual.
Created Date: December 15,2017
Created by: Do-more PE
We are working on getting cables as accessory items. I wish it were as simple as waving a magic wand, but unfortunately it is a bit more complicated than that. ;)
As far as the diagrams in the manual or help file, that isn't my product line so I can't comment on why they are not there.