adccommunitymod (AutomationDirect) asked a question.

Change Screen EA1-S3MLW

Created Date: October 04,2017

Created By: h2os

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Send command to change screen (PLC to Panel) does not change the screen. IF I change the screen from 2 to 3 and I want to go back from 3 to 2 it will not let me. But if I go to screen 4 it will let me go back to 2. Using V2000 as change screen address and V2004 as the current screen address; when it does not work the values are V2000 = 2 & V2004 = 3


  • adccommunitymod (AutomationDirect)

    Created Date: October 04,2017

    Created by: h2os

    Send command to change screen (PLC to Panel) does not change the screen. IF I change the screen from 2 to 3 and I want to go back from 3 to 2 it will not let me. But if I go to screen 4 it will let me go back to 2.

    Using V2000 as change screen address and V2004 as the current screen address; when it does not work the values are V2000 = 2 & V2004 = 3

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 04,2017

    Created by: Do-more PE

    The Panel has to see a change in the number. If you have a 2 loaded into V2000 and put another 2 in it, it's just going to sit there as nothing has changed as far as the panel can tell.

  • adccommunitymod (AutomationDirect)

    Created Date: October 04,2017

    Created by: bcarlton

    Use a rung of logic - if the current screen number is equal to the requested screen number then move a non-used screen number (don't use zero) into the requested screen number. Make sure to one-shot the orinal screen request rungs so that they aren't trying continously writing the screen request number.

  • adccommunitymod (AutomationDirect)

    Created Date: October 05,2017

    Created by: kewakl

    I am reading OP a bit differently.

    I am thinking that OP is changing from screen 2 to screen 3, then desiring to go back to screen 2 -- from screen 3.

    If OP is using a mix of PLC commands and HMI Screen Change objects, then he can get into this situation.

    To further flesh-out Bernie's suggestion:

    ---DirectLogic

    .

    . V2000 V2004 | LD

    .----------------------]=

    In one rung you will get the 'one-shot ' effect that Bernie mentioned, and the register change that Do-more PE mentioned.

    ---DoMore

    .

    . V2000 V2004 |Move

    .----------------------]=

    What happens is '9999 ' is (probably) not a valid screen number for your application, the hmi will silently fail to change to a non-existent screen. And you will get a new number in the ScreenChange register so that when you wish to go back to screen 2, that register will hold a 9999, so the new '2 ' will be recognized as a value change.

    As Bernie states, do not use ZERO, that is interpreted as PREVIOUS SCREEN.

    EDIT: remove wayward '+ ' in ascii rung

    Expand Post