Could Somebody Help me: I have a Direct Logic 06 PLC that is reading an analog Signal that is saved in the variable V2000. I want convert this data to an unit of engineering (Pressure) and send it to HMI. To do it, I need perform the next mathematical operation, but I dont know that instrucction o logic must use: (V2000 * 0.007082) -14.5. The result will send to a HMI. Please, Could you help me? Regards
Created Date: May 09,2017
Created by: ja_varela77
Could Somebody Help me:
I have a Direct Logic 06 PLC that is reading an analog Signal that is saved in the variable V2000.
I want convert this data to an unit of engineering (Pressure) and send it to HMI.
To do it, I need perform the next mathematical operation, but I dont know that instrucction o logic must use:
(V2000 * 0.007082) -14.5.
The result will send to a HMI.
Please, Could you help me?
Regards
Created Date: May 10,2017
Created by: bcarlton
If the reading is in the BCD format you must first use the BIN command to change it to the 'binary ' form. (The BCD command would not be needed if the reading is already in the binary format.)
Then use BTOR to convert this to a REAL (floating point) format.
Then use MULR with an argument of R0.007082
Then use SUBR with an argument of R-14.5
At this point the REAL format result is in the accumulator occupying 32 bits
Use the OUTD command to send the result to 2 adjacent 'V ' memory registers (eg OUTD V2000 would send the result to V2000 and V2001)
Created Date: May 11,2017
Created by: ja_varela77
Hi Bernie
Thank so much for your help.
Now all is clear.
My mistake was not use the instruction BTOR.
Best Regards