Are Ethernet communications between the new Click (with Ethernet) the (old) C-More EA7 screens not supported?


  • adccommunitymod (AutomationDirect)

    Created Date: February 27,2017

    Created by: LBM

    Are Ethernet communications between the new Click (with Ethernet) the (old) C-More EA7 screens not supported?

  • adccommunitymod (AutomationDirect)

    Created Date: February 27,2017

    Created by: jackson

    You have to use the "Modicon Modbus TCP/IP Ethernet " driver and use the Modbus 984 Addressing (In CLICK software, go to Address Picker and enable "Display MODBUS Address "). The CLICK Ethernet units came out after EA9 was released.

  • adccommunitymod (AutomationDirect)

    Created Date: February 27,2017

    Created by: kewakl

    You have to use the "Modicon Modbus TCP/IP Ethernet " driver and use the Modbus 984 Addressing (In CLICK software, go to Address Picker and enable "Display MODBUS Address "). The CLICK Ethernet units came out after EA9 was released.

    and it looks like we will not get a V2.78 SP2 :(