adccommunitymod (AutomationDirect) asked a question.
Created Date: January 18,2017
Created By: Trilo68
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
For some reason none of my indicator or bitmap buttons are working correctly. Here is what I have: A bitmap button using the same tag for button and indicator. When pressing the button on the HMI, I get a PLC service error (PLC-498), and the bitmap does not change. However if I go into the PLC and toggle the bit, the bitmap changes. It seems like reading the tag is fine but writing is not. This is happening with all my bitmap and indicator buttons. I have tried Toggle, Momentary On and Set on types. I have also tried FW 6.20 6.21 and 6.30. This project is merely a copy for an identical machine, which worked fine. Every component is identical except the original screen came flashed with 6.20 and the new one 6.30, but I have already tried downgrading with no luck. PLC is Micrologix 1400 over Ethernet/IP, HMI is EA9-T8CL. Any suggestions?
Created Date: January 18,2017
Created by: Trilo68
For some reason none of my indicator or bitmap buttons are working correctly. Here is what I have:
A bitmap button using the same tag for button and indicator. When pressing the button on the HMI, I get a PLC service error (PLC-498), and the bitmap does not change. However if I go into the PLC and toggle the bit, the bitmap changes. It seems like reading the tag is fine but writing is not. This is happening with all my bitmap and indicator buttons. I have tried Toggle, Momentary On and Set on types.
I have also tried FW 6.20 6.21 and 6.30. This project is merely a copy for an identical machine, which worked fine. Every component is identical except the original screen came flashed with 6.20 and the new one 6.30, but I have already tried downgrading with no luck.
PLC is Micrologix 1400 over Ethernet/IP, HMI is EA9-T8CL.
Any suggestions?
Created Date: January 18,2017
Created by: OkiePC
What is the address assigned to the button? Could it be set to read only in the HMI software or set to Local or Static in the PLC?
Created Date: January 19,2017
Created by: rguimond
Just tried replicating your problem, but it works fine. The only difference is I'm using a EA9-T10CL and, of course, the PLC memory addresses are probably different.
Out of curiosity, you 're not trying to directly address an output, are you?
Created Date: January 21,2017
Created by: johnaden
When I get a PLC 498 error using a Micrologix, it usually is that the PLC files are not opened up enough. Try adding a first rung with a MOV to a file addressed higher than the HMI addresses you are using.
Created Date: January 23,2017
Created by: rguimond
When I get a PLC 498 error using a Micrologix, it usually is that the PLC files are not opened up enough. Try adding a first rung with a MOV to a file addressed higher than the HMI addresses you are using.
Do you mean that the addresses being requested by the HMI don't exist in the PLC program?
Created Date: January 23,2017
Created by: johnaden
Yes, that is the problem that I have experienced.
Created Date: January 24,2017
Created by: rguimond
Yes, that is the problem that I have experienced.
I just tried it and got the same error. The OP must have attached the wrong address to the tag. I 've done it too many times to count...