adccommunitymod (AutomationDirect) asked a question.

Need help mirroring Cmore HMI

Created Date: December 27,2016

Created By: Huntxtrm

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have 2 ea7-s6m panels operating one Click C0-00DR-D. I am having trouble with communictation between one of the panels and the PLC. It will not operate the plc. It shows error message "PLL007 DEV002 CRC does not match "? I have it connected as follows. Laptop to com1 of the plc. HMI 1 to com2 of plc via EA-2CBL-1. From that HMI Ethernet port to Ethernet 5 channel switch. From Switch to HMI 2 via EA-2CBL-1. and then from Switch to Ethernet port on HMI 2. Any help would be appreciated.


  • adccommunitymod (AutomationDirect)

    Created Date: December 27,2016

    Created by: Huntxtrm

    I have 2 ea7-s6m panels operating one Click C0-00DR-D. I am having trouble with communictation between one of the panels and the PLC. It will not operate the plc. It shows error message "PLL007 DEV002 CRC does not match "? I have it connected as follows. Laptop to com1 of the plc. HMI 1 to com2 of plc via EA-2CBL-1. From that HMI Ethernet port to Ethernet 5 channel switch. From Switch to HMI 2 via EA-2CBL-1. and then from Switch to Ethernet port on HMI 2. Any help would be appreciated.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: December 27,2016

    Created by: Huntxtrm

    Possibly one is supposed to be a slave and the other a master? But, I cant figure out how to set that up.

  • adccommunitymod (AutomationDirect)

    Created Date: December 27,2016

    Created by: Mike Nash

    When you are choosing how to connect in Panel Manager for the indirect panel, you will need to choose "Connect through another panel ". I have never actually done this though and now my copy of v2.78 has decided to crap out so that's all I have, sorry.

  • adccommunitymod (AutomationDirect)

    Created Date: December 28,2016

    Created by: Huntxtrm

    Thanks for the Help.. I'll give that a try. I think maybe I have a wiring problem. I have a rj45 Ethernet on the switch end, and an rj12 RS232 on the plc end? I might have the pinout wrong? Should the pairs stay the same? starting at the middle of the plug?

  • adccommunitymod (AutomationDirect)

    Created Date: December 29,2016

    Created by: Huntxtrm

    Here is how it is cable up now. I didn't do it. LOL. I knew something wasn't right. lol

  • adccommunitymod (AutomationDirect)

    Created Date: December 29,2016

    Created by: Huntxtrm

    Here is the panel manager screen. It only show me one panel. I am confused as to how to set them up through here as you instructed?