adccommunitymod (AutomationDirect) asked a question.

P2K TCP/IP to C-More 8" EA9

Created Date: November 25,2016

Created By: ssjophus

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I am having trouble figuring out how to set up communication over ethernet between a P2K and C-More 8 " EA9. I figured it out on a click pretty easily, but this is way over my head. I'm sure there is no shortage of people who are smarter than me that can tell what I am doing wrong.


  • adccommunitymod (AutomationDirect)

    Created Date: November 25,2016

    Created by: ssjophus

    I am having trouble figuring out how to set up communication over ethernet between a P2K and C-More 8 " EA9. I figured it out on a click pretty easily, but this is way over my head. I'm sure there is no shortage of people who are smarter than me that can tell what I am doing wrong.

  • adccommunitymod (AutomationDirect)

    Created Date: November 25,2016

    Created by: andremholmes

    Is 192.168.11.200 the IP address of the P2K?

  • adccommunitymod (AutomationDirect)

    Created Date: November 25,2016

    Created by: ssjophus

    Yes and 192.168.11.57 is the IP address for the C-More. Local Network through a Stride SE-SW5U switch. No Internet accessability.

  • adccommunitymod (AutomationDirect)

    Created Date: November 25,2016

    Created by: andremholmes

    The help of the C-More panel say this "Verify the PAC communication port settings are the same as the C-more panel. "

  • adccommunitymod (AutomationDirect)

    Created Date: November 25,2016

    Created by: Ridgeline Mach

    You do not need to create a generic Ethernet client in the P2K to communicate between the P2K and C-more. Just make sure you choose "AutomationDirect Productivity Ethernet " for the PLC protocol in your C-more.

  • adccommunitymod (AutomationDirect)

    Created Date: November 25,2016

    Created by: ssjophus

    I tried it without the generic client first and i had the same result. This may be related, I can see the plc through suite via ethernet but I cant connect to it through ethernet. I can only connect through USB. When I try to connect through ethernet I get an IP setup conflict (see attachment), I just havn't been able to find the conflict.

  • adccommunitymod (AutomationDirect)

    Created Date: November 26,2016

    Created by: ssjophus

    It is within range (192.168.11.98). I also tried connecting direct (without the switch). Im beginning to wonder if there is a problem with the ethernet end of the PLC.

  • adccommunitymod (AutomationDirect)

    Created Date: November 26,2016

    Created by: Do-more PE

    Your P2k address is set to 162 .168.11.200, not 192 .168.11.200.

  • adccommunitymod (AutomationDirect)

    Created Date: November 27,2016

    Created by: ssjophus

    Well I feel stupid now. Thank all of you for your help.

  • adccommunitymod (AutomationDirect)

    Created Date: November 27,2016

    Created by: kewakl

    Well I feel stupid now. Thank all of you for your help.

    It is a common feeling, don't let that stop you.